I’m wiring a Rheem Crosswind 50-I pool heater. I installed a 2 pole 20A GE GFCI circuit breaker that is HACR rated. The unit will start but when the compressor turns on, the breaker trips.
The unit only requires 240v with no neutral. The pigtail of the GFCI breaker is on the neutral bar of a sub panel with separated neutrals and grounds.
Any help is appreciated.
The unit only requires 240v with no neutral. The pigtail of the GFCI breaker is on the neutral bar of a sub panel with separated neutrals and grounds.
Any help is appreciated.