Rheem water heater 3 phase chart calculation question
Looking at the chart from RHEEM water heater installation manual for recommended ocd 3 phase 480 breaker and wire. I do not see how they came up with the calculation for them, as they are alot higher. I am curious how they wired their heating elements in them, and how many heating elements. most have 2 heating elements, but I have seen 1.
One example is the 12000 watt 3 phase 480 volt. They require 30amp ocp and #10 wire. Why do they need a 30amp? 12000/(480x1.73) =14.45 14.45x1.25=18.06
If they have 2 heating elements, and wired most of them in open deltas, I think I can see the difference in calculation. also, the 9000 watt total tank. 9000/(480x1.73)= 10.838 10.838x1.25= 13.547amps. Yet they want a 25amp ocp and # 8 wire. Why the 25amp?
I suppose if they used 2 heating elements at 4500watts each, to get the 9000, then each heating element will most likely be at single phase calculation. 4500watt/480 =9.375amps 9.375x1.73 =16.21875amps for one of the phases if wired in an open delta configuration, then 16.21875 x 1.25 (ocp) =20.273 minimum ocp. Max ocp 1.5 x 16.21875=24.328 next size up 25 amp.
Am I correct in this assumption?
Why the 25amp?
If both WH elements are always interlocked, only one operates at a time.
That chart applies to single phase elements, so their calculation is correct without any Delta or 1.732 factors.
9kW / 480 * 1.25 = 23.44A or 25A fuse
12kW / 480 * 1.25 = 31.25A or 35A fuse
But back to my original question, am I correct in this thinking in how they came up with the calculation?
I don't know enough about the construction to say you are correct, but I can confirm your computations assuming that the 3 phase version uses (2) 2-wire heating elements that may be energized simultaneously. So I infer you are correct.
Cheers, Wayne