Re: RHO derating factors
Originally posted by rbalex:. . . where would I not calculate a load per 220?
Good question. Forgive my answer being a bit long and complex.
Suppose you design an office building. You perform a service calculation (per NEC 220) for the core and shell and the first four tenants. You get a calculated result of 1650 amps, but you know that the actual load will be lower. The owner tells you there is room for at least two more tenants. You select a 1,500 KVA transformer (480/277V secondary), and a 2000 amp main board. Using Table 310.16, you select five sets of 500 MCM THHN Copper. You calculate the ampacity at 5 x 380 = 1900. You select a 2000 amp main frame breaker, and set the trip at 1900 amps. At the beginning of this project, the cables are sized for 1900 amps, and the calculated service load is 1650.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Question 1: Is this design acceptable?</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
A year later, two new tenants prepare to move in. You perform a 30 day load study, and discover the actual peak load is closer to 1200 amps. Add 25% for conservatism, and call the existing load 1500 amps. You perform a service calculation for the two new tenants, and conclude they will add 300 amps to the total load. You add the 1500 to the 300, and your result is still below the 1900 amp setting of the main breaker.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Question 2: Is this design change acceptable?</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
My answer to the first question is ?yes, but with some reservations.? That is because I have looked at Table B.310.7. Using that table (not a code requirement), I see that 5 sets of 500 MCM THHN Copper in a six-way ductbank, using a RHO of 90, and a Load Factor of 100%, will give me an ampacity of 5 x 273 = 1,365 amps. That is below the calculated result of 1650 amps, but I also know that the calculation method is conservative, and that the actual load will be much lower.
My answer to the second question is ?no.? First, it is clear that the total calculated load is 1650 (original) plus 300 (new tenants), for a total of 1950, and that the conductors are only sized for 1900 amps. You might argue that you have new information, that the actual load is less than the original 1650, so that you should have capacity to add 300 more, and still be less than the 1900 amps. I counter-argue that you would be mixing the concepts of NEC-220 calculated load and the concept of measured load. The measured load is already too close to the 1365 amps that I would get from B.310.7. I don?t see any room for the addition of 300 more amps, even if that is just the 220 calculation, and even if I know the actual new load addition would be less than 300 more amps.