Hi All,
I am installing a new sub-panel and 2/3 SER feeder to a third floor location. I found a preexisting 1.5 ridged metal conduit sleeve to runs from the basement to third floor. The conduit will have fittings with bushings on each end with no connection to either the main or sub-panel.
I typically would use PVC in an application like this.
My concern should the ridge metal conduit sleeve be grounded?
I could install a large metal j-box strip on one end and run the SER through that first to bond it if necessary.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
As a conduit yes,
As a sleeve no

If there is a likelihood of becoming energized. YES
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If it qualifies as a sleeve under 250.86 then connection to an EGC is not required.

250.86 Other Conductor Enclosures and Raceways. Except as permitted by 250.112(I), metal enclosures and race-
ways for other than service conductors shall be connected to the equipment grounding conductor.
Exception No. 1: Metal enclosures and raceways for conductors added to existing installations of open wire, knob-
and-tube wiring, and nonmetallic-sheathed cable shall not be required to be connected to the equipment grounding
conductor where these enclosures or wiring methods comply with (1) through (4) as follows:
(1) Do not provide an equipment ground
(2) Are in runs of less than 7.5 m (25 ft)
(3) Are free from probable contact with ground, grounded
metal, metal lath, or other conductive material
(4) Are guarded against contact by persons
Exception No. 2: Short sections of metal enclosures or
raceways used to provide support or protection of cable
assemblies from physical damage shall not be required to
be connected to the equipment grounding conductor.

Exception No. 3: A metal elbow shall not be required to be
connected to the equipment grounding conductor where it
is installed in a run of nonmetallic raceway and is isolated
from possible contact by a minimum cover of 450 mm
(18 in.) to any part of the elbow or is encased in not less
than 50 mm (2 in.) of concrete.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Yep, like subject to physical damage and such. NFPA leaves it up to each AHJ to decide what is acceptable.

In your opinion, should be 0P make sure that sleeve is grounded? Just in case his AHJ has a quirk and decides that it's not a short piece.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
That is way to subjective of a question for me to offer an opinion to the OP.

Since I not know all the variables, I could easily get slammed for saying yes or no.

I will pass.:)
OK no problem. I was just asking for an opinion. No one's answers here in this forum are 100% correct and carved in granite. No one is looking to hang you out to dry
 