On Monday I will be part of a group visiting a plant where styrofoam plates and food packaging are made.
The principal controls reported are Yaskawa A1000 VFDs https://software.yaskawa.eu.com/en/...he-high-performance-drive/specifications.html and Siemens PLC S7-1500 CPU (PLC) Part number 6ES7-515-2AM01-0AB0 https://mall.industry.siemens.com/mall/en/WW/Catalog/Product/6ES7515-2AM01-0AB0
Service is provided by the POCO's 4200kVA, three phase transformer, 480/277Y.
This plant uses an extrusion process to create their product.
The problem is this plant's process cannot ride through a utility substation breaker operation. The reclose time on the POCO's first operation is 1 second.
We have heard stories that if there is a significant voltage sag to their equipment, they have similar problems. These sags are typically caused by primary faults on the POCO's lines that sag their power transformer voltage at the substation for the time it takes their OCPD to clear that fault.
What options are available that will allow this plant to ride through these types of events?
We have talked about UPS and similar high cost options. This plant peaks above 3MVA. Our role is to look at their equipment, gather information and make recommendations.
The principal controls reported are Yaskawa A1000 VFDs https://software.yaskawa.eu.com/en/...he-high-performance-drive/specifications.html and Siemens PLC S7-1500 CPU (PLC) Part number 6ES7-515-2AM01-0AB0 https://mall.industry.siemens.com/mall/en/WW/Catalog/Product/6ES7515-2AM01-0AB0
Service is provided by the POCO's 4200kVA, three phase transformer, 480/277Y.
This plant uses an extrusion process to create their product.
The problem is this plant's process cannot ride through a utility substation breaker operation. The reclose time on the POCO's first operation is 1 second.
We have heard stories that if there is a significant voltage sag to their equipment, they have similar problems. These sags are typically caused by primary faults on the POCO's lines that sag their power transformer voltage at the substation for the time it takes their OCPD to clear that fault.
What options are available that will allow this plant to ride through these types of events?
We have talked about UPS and similar high cost options. This plant peaks above 3MVA. Our role is to look at their equipment, gather information and make recommendations.