I have a pendent crane hoist that is rated for 4 Amps at 480V. Because of its location the only way we have avaliable to power it is with a 20A 480V breaker. The contractor supplied 16AWG wire which is rated less then 20A.
I'm telling him that he cannot use wire that is rated less than the rating on the feeder breaker to run this circuit. I believe #16 is rated for 15A which is below the rating of the breaker. Am I correct in telling him that this wire although sized ok for this load, is still not sized correctly for the avaliable breaker size?
Does it matter that this is not a continuous load but rater an intermitent non-continuous load?
I'm telling him that he cannot use wire that is rated less than the rating on the feeder breaker to run this circuit. I believe #16 is rated for 15A which is below the rating of the breaker. Am I correct in telling him that this wire although sized ok for this load, is still not sized correctly for the avaliable breaker size?
Does it matter that this is not a continuous load but rater an intermitent non-continuous load?