Hugh W
Member
- Location
- Mebane, NC
I'm beginning a project that will require an 800A/480VAC feeder to a panel board and the conduits will be 500MCM paralleled feeds with 1/0 grounding conductors. The total area for (3) THHN 500MCM and (1) THHN 1/0 is 3.333 sq. in., which will require a 3-1/2" RMC per 40% fill in Chapter 9 Table 4 Article 344, but Annex C Table C.8 indicates (4) 500MCM's can be installed in 3" RMC.... so which is correct?
Thanks,
Hugh Wright
Thanks,
Hugh Wright