j rae said:Are the threads on rigid conduit threaded??? I belive so but some conterversy!
Do you mean cut as opposed to rolled?j rae said:Are the threads on rigid conduit threaded???
No, but rigid pipe is.ultramegabob said:is ridgid pipe really ridgid???:grin:
j rae said:Are the threads on rigid conduit threaded??? I belive so but some conterversy!
Factory threads on RMC are machine cut... as opposed to molded, or some other type of fabrication.j rae said:Are the threads on rigid conduit threaded??? I belive so but some conterversy!
TOOL_5150 said:Is this a trick question? :-?
Conduit is threaded with a threader, it does not have the same taper as water pipe though. RMC can also be cut and a compression connector can be put on which converts pipe to threads.
~Matt
If you mean with a needle, then no it isn't.:grin:j rae said:Are the threads on rigid conduit threaded??? I belive so but some conterversy!
It does have the same taper!TOOL_5150 said:Is this a trick question? :-?
Conduit is threaded with a threader, it does not have the same taper as water pipe though. RMC can also be cut and a compression connector can be put on which converts pipe to threads.
~Matt
Welcome to the Forum, J. Rae.j rae said:Are the threads on rigid conduit threaded??? I belive so but some conterversy!
Water pipe and electrical conduit have the same taper, dies sold by Ridgid are only available in one type.TOOL_5150 said:Is this a trick question? :-?
Conduit is threaded with a threader, it does not have the same taper as water pipe though. RMC can also be cut and a compression connector can be put on which converts pipe to threads.
~Matt
tom baker said:Water pipe and electrical conduit have the same taper, dies sold by Ridgid are only available in one type.
But a water pipe coupling has a taper and an electrical does not.If you mix the two - like I did once- it will leak.
infinity said:Actually there are two types of dies both sold by Rigid. NPT- National Pipe Thread which are tapered and NPSM-National Standard Free-Fitting Straight Mechanical Pipe Thread. The latter is sometimes called "the Straight Electrician's Thread" even though the NEC requires the use of field cut tapered threads.
ultramegabob said:I used to work for a company who used the straight threaders, people keep telling me they dont make them or all pipe threads are taperd, I knew I wasnt crazy:grin:
infinity said:Actually there are two types of dies both sold by Rigid. NPT- National Pipe Thread which are tapered and NPSM-National Standard Free-Fitting Straight Mechanical Pipe Thread. The latter is sometimes called "the Straight Electrician's Thread" even though the NEC requires the use of field cut tapered threads.
ultramegabob said:the thing about a tapered thread is the locknuts cant chase all the way down, and it makes it hard to land in a box set another lock nut inside and be able to fit a bushing on what is left....
j rae said:Are the threads on rigid conduit threaded??? I belive so but some conterversy!