If I install RMC under ground and before I emerge from grade change to pvc is this ok as long as the RMC is completely buried in the whole run and a separate equipment ground is run to the equipment? I am going to be running rmc for a hot tub due to a tree the customer loves and i do not have much choice to dig nearby. my inspector said he would except the 6 inch deep rule. If not I was thinking direct burial pipe clamps on both sides and bonding it. I dont know why I am under the impression that if its all buried and separate equipment ground run its OK.
instead of burying pipe clamps, run GRC all the way to one end or the other, and use a ground bushing on that end,
pull a ground wire, and be done with it.
so it stays there and doesn't rust away, you gonna tape it up with scotchwrap?
i've had duct banks that crossed other duct banks, and had to go over the top,
and get within 6" of roadway, and the solution was to use GRC, build the 27 3"
pipes as 4 point saddles, with unistrut racking, outside the ditch, and then lower
the entire thing in the ditch with a crane, hanging it off running thread with strut
across the ditch, and pouring 2,500# concrete over it, encasing it with 2" on all sides,
then remove the strut across the top and cut off the running thread below grade, and patch it.
it was pvc on both sides, and there wasn't any bonding done to it, as it was encased
and not accessible.