rigid pendant?

Status
Not open for further replies.

mek421

Member
Location
Upstate NY, USA
I'm an occupational health and safety consultant. One of my clients has rigid steel drops to receptacle boxes the are about 10 - 15 feet (3 - 5 m) from the ceiling that terminated to steel receptacle boxes. These boxes* caught my eye because they have knockouts* that I know are inappropriate for flexible cord use.

Where in NEC should I be reading to find out if these rigid drops are ok to begin with, and, if so, whether the existing steel boxes are ok?

* similar to this: Home Depot steel receptacle box

Thanks!
 
I'm an occupational health and safety consultant. One of my clients has rigid steel drops to receptacle boxes the are about 10 - 15 feet (3 - 5 m) from the ceiling that terminated to steel receptacle boxes. These boxes* caught my eye because they have knockouts* that I know are inappropriate for flexible cord use.

Where in NEC should I be reading to find out if these rigid drops are ok to begin with, and, if so, whether the existing steel boxes are ok?

* similar to this: Home Depot steel receptacle box

Thanks!

I don't think it is OK. I believe more than one code rule is being broken, but you can start with 344.30(B) Next it violates 314.23(F)
 