Rigid PVC Conduit Annex C 2017 NEC
goldstar
New Jersey
Electrical Contractor
Can anyone explain the differences between these types of PVC conduits ?
C.10 — Rigid PVC Conduit, Schedule 80
C.10(A)* — Rigid PVC Conduit, Schedule 80
C.11 — Rigid PVC Conduit, Schedule 40 and HDPE Conduit
C.11(A)* — Rigid PVC Conduit, Schedule 40 and HDPE Conduit
C.12 — Type A, Rigid PVC Conduit
C.12(A)* — Type A, Rigid PVC Conduit
C.13 — Type EB, PVC Conduit
C.13(A)* — Type EB, PVC Conduit
I was asked by one of my colleagues which type would be approved for use in direct burial in cement.
Thanks in advance
Not sure what Types A and EB are, but I can tell you Schedule 80 has a thicker wall than Schedule 40.
In cement, I see PVC basically as a stay-in-place form, so I'd go with regular Schedule 40 PVC conduit.
Type EB and A conduit and fittings
1.3.1 The Type EB and Type A rigid PVC conduit and fittings mentioned in 1.1.1 are intended for use at 50°C (122°F) and lower ambient temperatures. Type A rigid PVC conduit and fittings are intended for use with 75°C (167°F) wiring. Type A and Type EB rigid PVC conduit and fittings, where encased in concrete in trenches outside of buildings, may be used with 90°C (194°F) wiring.
1.3.2 Type EB (encased burial) rigid PVC conduit is intended for encasement in concrete in trenches outside of buildings. Type A rigid PVC conduit is intended for encasement in concrete in any location.