Rigid steel conduit elbows. Do you find this as a spec requirement often? Reasons for or against? Direct buried conduit versus concrete encased duct bank make a difference? Alternative measures to address the main concerns? Good value engineering suggestion to change to PVC?
 
Presuming just the elbows, for pulling conductors without damage that might happen with PVC elbows.
 
Rigid steel conduit elbows. Do you find this as a spec requirement often? Reasons for or against? Direct buried conduit versus concrete encased duct bank make a difference? Alternative measures to address the main concerns? Good value engineering suggestion to change to PVC?


Yes, it is almost a universal specification in the oil and gas industry. It definitely helps for pulling at the 90 degree stub-up and horizontal bends. The concrete stabilizes and protects the conduit.
 
Presuming just the elbows, for pulling conductors without damage that might happen with PVC elbows.


I've seen PVC elbows break during concrete pour at stub-ups, particularly smaller diameter under 2". Its also a bit more logical to transition (PVC to rigid steel) below grade rather than above - that is if you're going vertically into a piperack, cable tray or building after you stub-up.
 