Hey guys I have job coming up to add a circuit in the middle of a concrete floor to feed two ice cream frigs. Concrete is removed for the drain going in and I want to use the same ditch and then they will fill back up with concrete and I will wrap with 10 mil.
Can I use rigid conduit as the support for this box? If so can it be one piece of rigid or two out of the box? 1/2" by the way.
How close can it be to the drain? I think right next if GFCI protected.
I'am worried the inspector will say it is a trip hazard, but it is right up against the machine, but workers will be walking behind the machine, to other equipment.
What code section is this under?
Thanks guys for any input.
Can I use rigid conduit as the support for this box? If so can it be one piece of rigid or two out of the box? 1/2" by the way.
How close can it be to the drain? I think right next if GFCI protected.
I'am worried the inspector will say it is a trip hazard, but it is right up against the machine, but workers will be walking behind the machine, to other equipment.
What code section is this under?
Thanks guys for any input.