jazer
Senior Member
- Location
- Gibsonia, Pa
I have a situation where rigid steel is used in straight runs after penetrating a roof, then transitions to LFMC to compensate for bends, then transitions back to rigid for more straight runs, then, finally, transitions back again to LFMC to hit the disconnect for the equipment on the roof. An equipment ground conductor is run with the circuit conductors. My problem with this is that there is more than 6' of LFMC in this run. I understand that the equipment and enclosures and such are bonded correctly with the seperate EGC, but the rigid raceway seems like it would lose its bonding continuity with more than 6' of LFMC? The raceway is 1 1/4". I am referencing 350.60, then 250.118(6). The circuit meets the requirements of 250.18(6). I guess my ultimate concern is losing the electrical continuity (bonding) of the raceway. Any help?