K KIPTOO998 Member Location Kenya Occupation Technician Jul 12, 2020 #1 What is the maximum current for a fully loaded ring circuit with 13amps sockets fully loaded .want to load a tent 50square metres with 13 twin socket
What is the maximum current for a fully loaded ring circuit with 13amps sockets fully loaded .want to load a tent 50square metres with 13 twin socket
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jul 12, 2020 #2 This is an NEC forum and here in the US we do not use ring circuits.
K KIPTOO998 Member Location Kenya Occupation Technician Jul 14, 2020 #3 tom baker said: This is an NEC forum and here in the US we do not use ring circuits. Click to expand... What do you use ?
tom baker said: This is an NEC forum and here in the US we do not use ring circuits. Click to expand... What do you use ?
Coppersmith Senior Member Location Tampa, FL, USA Occupation Electrical Contractor Jul 14, 2020 #4 The receptacles are connected to the power source at one point only. If you were to break a ring circuit at any point, you would have what we do.
The receptacles are connected to the power source at one point only. If you were to break a ring circuit at any point, you would have what we do.