Working in a manufacturing plant on a 480V (Wye) supplied cabinet that has a PLC controller for a nickel plating line along with a various control relays, etc. On the outside of the cabinet is mounted a 480V-120V transformer (2 wire secondary) that supplies control circuits as well as a boiler circulation motor.
The secondary of this transformer is not grounded (which is what I am going to do). I noticed rather than using a ground bus bar, the person who wired it took all the grounds to a 1/2" stud on the galvanized base plate in the cabinet. There are about 5 ground wires ranging 14 to 10ga crimped into ring terminals and put on the one stud. Is there any restriction that limits how many ring terminals on one stud? I have not found anything in the NEC handbook. I am inclined to put in two bus bars; one for the grounds, and one for the "neutral" of the transformer and then bond the two together. Any thoughts? Thanks
The secondary of this transformer is not grounded (which is what I am going to do). I noticed rather than using a ground bus bar, the person who wired it took all the grounds to a 1/2" stud on the galvanized base plate in the cabinet. There are about 5 ground wires ranging 14 to 10ga crimped into ring terminals and put on the one stud. Is there any restriction that limits how many ring terminals on one stud? I have not found anything in the NEC handbook. I am inclined to put in two bus bars; one for the grounds, and one for the "neutral" of the transformer and then bond the two together. Any thoughts? Thanks