GC said they are boxing out the slab for these conduits and MC cables. Would the slab evenbtually get poured around these? No sloeeving would be required except for MC cables? THis is a plan view of vertical raceways/cables.

1717679479648.png
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Unless the GC agrees to go back and have the concrete mason pour around those conduits and cables they're typically filled in with firestop. Personally I like when they leave a slot opening because additional conduits and cables can be added in the future without disturbing the concrete.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Unless the GC agrees to go back and have the concrete mason pour around those conduits and cables they're typically filled in with firestop. Personally I like when they leave a slot opening because additional conduits and cables can be added in the future without disturbing the concrete.
Have you ever seen concrete oured around a situation like this?
 