Riser Cable or Plenum cable in an interstitial space

Status
Not open for further replies.

jakeparsons03

Member
Location
USA
Occupation
Engineer
We have electricians who want to run control wire from a device back to the control panel by taking conduit up to an interstitial space then free-air running it back above a control panel and dropping it in conduit to the panel. The interstitial space is technically not a plenum as while it has Make Up Air units, they are piped to the outside and to the occupied space. There are exhaust fans on this level though. Do I need plenum cable or would riser cable work here.

I get the feeling that this is a gray area and it would depend on how your inspector is feeling that day.
 
If the space is used to convey air, whether heating/cooling or ventilation, it is considered an air handling or plenum space. Any cable run in that space must be plenum rated.

-Hal
 