electriciansnet
Member
Hey everyone. I got to trim a little fat and have permission to supplement feeders with ALU.

I feel a little dumb for asking this but since I'm not using a tap box and I'm going straight from the LL disconnect to the new Panel 'A', is there any reason why I cant use 2 sets of 4/0 and, (1) #2 ALU THHN in the 3" EMT or do I need to stay at 75 degree and use #250 (I can have up to 13).
Is the deration factor of more than 3 CCCs prohibitive of either of these factors?
Note:
The job is 5 hours away in Miami and I have not seen the LL equipment so I'm not sure if rejection clips are applicable so I have to assume that I have to full rate the feeders at 400

I feel a little dumb for asking this but since I'm not using a tap box and I'm going straight from the LL disconnect to the new Panel 'A', is there any reason why I cant use 2 sets of 4/0 and, (1) #2 ALU THHN in the 3" EMT or do I need to stay at 75 degree and use #250 (I can have up to 13).
Is the deration factor of more than 3 CCCs prohibitive of either of these factors?
Note:
The job is 5 hours away in Miami and I have not seen the LL equipment so I'm not sure if rejection clips are applicable so I have to assume that I have to full rate the feeders at 400