Risers and Strain Relief

Status
Not open for further replies.

Sean.Day72

Member
Location
Florida
I'm running riser cables from the 1st floor distribution panels to the 3rd floor panels of a parking garage. The plan is two run two 4" RMC conduits into a 24"W x 32"H pull box on the third floor. I used the 8x rule for sizing straight run pull box per NEC 314.28. Each 4" conduit will contain 8#1/0 , 2#6 wires (two circuits with 4 conductors and a ground ea.). I was planning on using Kellems grips to support each circuit and as way to separate them. The ones that look like a Chinese finger trap... Is there pull box you can order that comes with hooks already installed to hang the eye of the kellems grip on? Is there a better means to support the cables other than kellems grips? I looked into the chalks it doesn't seem pratical for this application. Also looked into support cleats but not sure how this would work with some many conductors in the pull box. Also if I'm missing a detail please let me know. Thanks for the help!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Kellems work but in my experience you should make the box nearly twice as long as the code minimum because they require quite a bit of vertical room. We always use chocks and chock bushings but for 10 conductors that might be a problem. When using Kellem grips we install our own support (eyebolt) either in the top or the back of the box.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I never used a common pull-box for cables in conduit. The last I designed -I hope it has been executed since no comment I received yet- was 10 RMC conduits of 3” from the ground to about 1000 ft-on a power-plant chimney.[all 100 ft. conduit pull box with Kellems strain relief grips].We used here conduits in order to avoid [fire] chimney effect.
They are expensive [and including conduit oulet [pull boxes] also].
For precipitator where there is an open air installation we used cable riser and Kellems cable support grips. The riser front is closed about 7 ft. from the floor and the floor is sealed with a kind of fire-stop. The front cover could be detached if necessary. All 100 ft[ about] a grips eye hanging device is fitted 4 ft. above the floor .
 