consider how bus duct is made--- a typical bus would have a single bus bar for each thousand amps it is rated for. a three thousand amp rated bus would have three insulated bus bars alongside each other for each phase. sometimes as a connection, or joint as it's called, fails maybe only one bar looses it's connection --- the load automatically shifts to the other two bars. and remember, this may only happen at certain load conditions. i have had bus ground out due to water -- blow maybe a three thousand amp fuse -- and blow itself free from the grounding surface. the maintainance staff didn't find the damaged section -- replaced the fuse and went back "on line". we found it during their two year infrared scan. it is very easy to scan bus ducts --- but you need the right camera and electrically inclined thermographer. when your looking at a 100 amp disconnect switch it is not uncommon to find five to ten degree temp. rise in the blade area when the equipment it servse it under full load. when it comes to bus duct, say 4000 amps, a one degree rise in a joint area needs attention. the newer cameras are not as sensitive as the original ---ya, there nice and light and computerized. i got used to the sensitivity of the old liquid nitrogen cooled units and didn't feel i was doing my customers proper service with the new units. pain to drag it up and down stairwells and ladders, but it produced a better service. a hospital is supposed to be scanned on some type of schedual --- bus duct should be scanned every two years and if problems are found, maybe yearly. it should not be that expensive. but if the operator doesn't know what to look for, or uses the wrong camera -- it's useless....................
ps: it doesn't take much water or even moisture to cause a bus duct explosion. we had a 2000 amp emergency bus blow up because an electrician who was using the office building's electrical closet as his office, installed a a/c duct into the electrical room from the corridor duct. took two years, but the cold air condensed enough moisture to cause the joint below the duct to fail. many building engineers and managers don't realize how critical it is to protect bus duct from moisture. in office buildings there should be a one to two inch collar built around all the bus duct floor penatrations to protect the bus if there is a flood from a broken pipe of sprinkler head. i always tell the engineers "you can pizz on this bus duct and blow it up"......................