N normbac Senior Member Dec 28, 2008 #1 when calculating the load on ac units do you use the RLA running load amps from the data on the compressor or? TIA
when calculating the load on ac units do you use the RLA running load amps from the data on the compressor or? TIA
wbalsam1 Senior Member Location Upper Jay, NY Dec 28, 2008 #2 normbac said: when calculating the load on ac units do you use the RLA running load amps from the data on the compressor or? TIA Click to expand... I would look first at 440.32, then see 440.6 (A) & (B), & Tables 310.16-19 or 310.15.
normbac said: when calculating the load on ac units do you use the RLA running load amps from the data on the compressor or? TIA Click to expand... I would look first at 440.32, then see 440.6 (A) & (B), & Tables 310.16-19 or 310.15.
mdshunk Senior Member Location Right here. Dec 28, 2008 #3 No, I'd use the dataplate on the condensing unit, and not worry too much about the compressor itself. It's too hard to see that dataplate anyhow.
No, I'd use the dataplate on the condensing unit, and not worry too much about the compressor itself. It's too hard to see that dataplate anyhow.
cadpoint Senior Member Location Durham, NC Occupation Electrician - but not by NC Law. Dec 28, 2008 #4 Use the nameplate ... or the aspects of it being "a" device, address accordingly, it's not a summary call.
Use the nameplate ... or the aspects of it being "a" device, address accordingly, it's not a summary call.