Did the inspector cite a code reference? Are you located in Nevada or other areas of the country where the AHJ and Locality has local rules for supplementary corrosion protection?
RMC already has protection as part of the evaluation process. Unless their is some local requirement I would visit
www.steeltubeinstitute.org and view their Q & A Area. Here is an excerpt from that site below. Note: The below information is openly posted and available at the aforementioned website above.
"The 2011 National Electrical Code (NEC) allows the direct burial of all three products as noted in their respective Articles:Galvanized Steel RMC Section 344.10 (B) Corrosion Environments. Galvanized steel RMC, elbows, couplings, and fittings ?shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.?
IMC Section 342.10 (B) Corrosion Environments. Galvanized steel IMC, elbows, couplings, and fittings ?shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.?
EMT Section 358.10 (B) Corrosion Protection. Galvanized steel EMT, elbows, couplings, and fittings ?shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and approved as suitable for the condition.?
Members of the Conduit Committee of the Steel Tube Institute apply a zinc coating to galvanize steel RMC, IMC and EMT. Therefore, these products are ?protected by corrosion protection? as the Code requires. However, in severe corrosive environments, the designer or AHJ may decide to require additional or supplementary protection.
Underwriters Laboratories? Guide Information for Electrical Equipment ? The White Book 2011 contains information relating to limitations or special conditions applying to products listed by UL. The Directory states that Galvanized steel RMC and IMC do not generally require supplementary corrosion protection when installed in soil unless: 1. Soil resistivity is less than 2000 ohm-centimeters. 2. Local experience has confirmed that the soil is extremely corrosive.
(Note: Soils producing severe corrosive effects have low electrical resistivity, expressed in ohm-centimeters. Local electric utilities commonly measure the resistivity of soils. The authority having jurisdiction (AHJ) has the authority to determine the necessity for additional protection.) EMT in direct contact with the soil generally requires supplementary corrosion protection. However, local experience in some areas of the country has shown this to be unnecessary."
Hope this was helpful.