A local high school is hosting a robotics competition and has gotten some sketchy info (IMO) on what the people that run the thing will be using to provide power. I do not know exactly what wiring method will be used, but from what I understand they have a 5c/#4 copper cable they want to connect to a 3 ph panel which is their distribution panel which will then feed (2), 1 ph panels via 4c/#6 cables. They eventually run some 20 A circuits for the kids to plug in computers and maybe some tools to work on their robots. Besides some other safety concerns, I wanted to be sure the ampacity of the feeders was not exceeded. Am I reading the table correctly in that for less than 100A, the 60 degree column is used, which would mean their #4 cable would need to be protected by a 70 A breaker max?
Also, that there should be no N/G bonds in any of the downstream panels?