I have a 1000 amp single phase service. It is feed from the PoCo w/ 3-4/0 alum per phase.
If I have a # 4Cu. ufer ground and 1 ground rod what size ground wire do I need.
If I read 250-66 right it would be 2/0 copper to the ground rod.
My Eng. is no help he wants to charge more $ For advise.
Some posts on this Forum say a fire riser is not to be used as a ground electrode per NFPA 13. I have been ask to remove the ground from the fire riser in the past.
The Eng. wants a 4/0 copper to the sprinkler main.He also wants 1 # 6 cu to a 3 rod Delta I think it needs to bond the sprinkler with 2/0 cu or 4/0 alum per 250-120
Can some help I think i'm going crazzy.
Thanks AL.
Thanks AL.