rods on rock
tommyrice
if i drove a ground rod vertically and hit solid rock,then pulled it back out and drove it at 45 degree angle and hit rock so that 1 foot still is above grade,could i bent top 1 foot over and cover it with dirt or would i have to lay rods horizontally 30" below grade?
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
8' is required to be below grade but I won't tell you that I have never cut a ground rod before in that situation. :grin:
mcclary's electrical
VA
I've beenin this situation, and the code proper way to do it is dig down 24", and bend it over horizontally. If you do this right at, or barely below grade, you will most likely not pass. I've tried it
infinity
New Jersey
Journeyman Electrician
The requirement is that you install the rod vertically 8' deep at an angle not greater than 45?. If this is not possible due to rock then you can bury the entire rod horizontally. I see no wording that would permit you to bend over and bury just the top portion of the rod.
250.53(G) Rod and Pipe Electrodes. The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10
VA
I was taught the way I posted above, after rereading, that's probably not correct. I see what you mean about the enire rod part, I never realized it said that.
realolman
I agree with the lack of specific wording, but I think it would be silly to not allow it. The whole rod would conform to one of the ways that are permissible.
infinity
New Jersey
What about plate electrode?
A big piece of metal buried in the ground. Here are the requirements:
250.52(A)(7) Plate Electrodes. Each plate electrode shall expose not less than 0.186 m2 (2 ft2) of surface to exterior soil. Electrodes of iron or steel plates shall be at least 6.4 mm (? in.) in thickness. Electrodes of nonferrous metal shall be at least 1.5 mm (0.06 in.) in thickness.
jxofaltrds
Mike P. Columbus Ohio
ESI
No do not bend the top.Yes you can bury it (them).
Look at exhibit 250.24 in the handbook.
wxstevens
Cool Ridge, WV
I couldn't tell you. I use 5/8 and 3/4 copper clad here as per specs and both are stamped. Anyone got a 5/8 galvie on the truck they could take a quick look at?
I am looking at a 5/8 with no marks.
