Does roll up generator 144kw 120/240 vac single phase usually come with overcurrent protection or would have to be provide it?

Sent from my SM-G935U using Tapatalk
 
Last edited:

ron

Senior Member
It almost always comes with it, but you would have no idea if a 144kW unit will roll up or a 200kW or some other size, so I always provide a OCPD at a roll up connection box to protect the feeder going into the building in case it is smaller than the roll-up.
 

publicgood

Senior Member
Location
WI, USA
It almost always comes with it, but you would have no idea if a 144kW unit will roll up or a 200kW or some other size, so I always provide a OCPD at a roll up connection box to protect the feeder going into the building in case it is smaller than the roll-up.

Concur
 