I've done it before, that doesnt make it right. Is it legal, or is your inspector a little lax? Didnt think states had the right to decide what part of the NEC they didnt want to adopt. Big brother is an SOG !
334.12(A)(2). Revise to read as follows:
(2) In dropped or suspended ceilings in other than one- and two-family and multifamily
dwellings, unless run so as to closely follow the surface of framing members, running boards,
or the equivalent, or unless connected to luminaires or other pieces of electrical equipment in
accordance with 334.30(B)(2).
YEP!
334.15 A 2 not allowed in OTHER THAN ONE AND TWO AND MULITIFAMILY DWELLINGS
334.15 A Follow the surface of the structure or on runners