I am studying a question as follows:
What size romex is required to supply a 6000va A/C unit?
6000/240v=25a
25a x 125% = 31.25a
The answer states at 75 deg., romex required would be #10 (35a). I thought you were limited to 60 deg. when dealing with romex because of 334.80? Am I missing something? Thanks.