N n84jrnation Member Location Piedmont South Carolina Usa Jun 1, 2017 #1 does romex have a spicific ampacity chart or does it fly on anything. i was told nm romex has to be on 60 degree ampacity.
does romex have a spicific ampacity chart or does it fly on anything. i was told nm romex has to be on 60 degree ampacity.
Ponchik Senior Member Location CA Occupation Electronologist Jun 1, 2017 #2 n84jrnation said: does romex have a spicific ampacity chart or does it fly on anything. i was told nm romex has to be on 60 degree ampacity. Click to expand... For derating purposes you can use the 90 degree column.
n84jrnation said: does romex have a spicific ampacity chart or does it fly on anything. i was told nm romex has to be on 60 degree ampacity. Click to expand... For derating purposes you can use the 90 degree column.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 1, 2017 #3 Check 334.80. It gives a detailed explanation of the ampacity and termination ratings.