romex clipped

Status
Not open for further replies.
On firing up a new circuit yesterday, it fired back. The problem traced down to a burr on the inside of the top part of a romex connector, apparently slicing into the hot conductor. My first thought was that there is really no way to have avoided this, but then I remembered that I had switched to a lower cost supplier. Now my chase nipples were 1/2" instead of 3/4", the flex connectors required a fight to make the fitting, etc.. You do get what you pay for!!
 

bphgravity

Senior Member
Location
Florida
Re: romex clipped

One sure test method is to check continuity between all the ungrounded conductors to the panel enclosure and/or EGC bar before energizing the circuits. This can save damaging the conductor, devices, and equipment from the high currents and arc flash that could result.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: romex clipped

Originally posted by problemsolver600:
On firing up a new circuit yesterday, it fired back. The problem traced down to a burr on the inside of the top part of a romex connector, apparently slicing into the hot conductor. My first thought was that there is really no way to have avoided this, but then I remembered that I had switched to a lower cost supplier. Now my chase nipples were 1/2" instead of 3/4", the flex connectors required a fight to make the fitting, etc.. You do get what you pay for!!
OTOH, you learned a cheap lesson on why you need to be careful when trying to save yourself a few bucks. While doing things the cheap way is often acceptable and provides for a decent installation, sometimes you get burned. Having to "fight" to make the fitting might have been a clue something was up. There are often good reasons (as well as not so good reasons) why things are commonly done in a certain way, even though there may exist less expensive ways of accomplishing the same thing.

:)
 