I have a exterior, surface mount electrical panel, and I have 18 romex circuits going into the back of it. I have 2, 2" nipples going through the back of it, into the wall with the romex going in. The inspector said that I cant have the romex entering the panel this way, and I have to have kno more than 3 wires, in a romex connector. What is the maximum amount of wires that can fit into a romex connector entering a panel? Any other suggestions, since the panel doesnt have that that much room inside to knock out many more holes? Thanks in advance for your response!
 

GerryB

Senior Member
I have a exterior, surface mount electrical panel, and I have 18 romex circuits going into the back of it. I have 2, 2" nipples going through the back of it, into the wall with the romex going in. The inspector said that I cant have the romex entering the panel this way, and I have to have kno more than 3 wires, in a romex connector. What is the maximum amount of wires that can fit into a romex connector entering a panel? Any other suggestions, since the panel doesnt have that that much room inside to knock out many more holes? Thanks in advance for your response!
Pretrty sure a twin screw romex conn. is two #12 or #14, not three. So he didn't like your nipples? Was it a bundling issue or that they were not secured? Could you put a j-box inside the building with the nipple connected to it and the romex entered into the j-box with connectors, then skin the romex and pass the conductors through the nipple. I would think that would be ok but I'm not sure.
 

JEI

Member
Location
CA
Pretrty sure a twin screw romex conn. is two #12 or #14, not three. So he didn't like your nipples? Was it a bundling issue or that they were not secured? Could you put a j-box inside the building with the nipple connected to it and the romex entered into the j-box with connectors, then skin the romex and pass the conductors through the nipple. I would think that would be ok but I'm not sure.

It's a bundle issue. It's all separated in the stud bay, then it goes through the nipples. There is kno space inside the structure, it's a shower inside of he building. I thought about a gutter under the panel, but I would still have same problem. I was wondering the code on 2 screw connectors an entering an exterior panel? I've done this in the past. If it's code it's code. Just seams a lot cleaner and better job not to have to knock out a bunch of 1/2 inch holes, like inspector wants.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In NC most areas will allow that install but it is not compliant. There really is not a good means of doing this. I have heard that there are some 2" romex connectors that will allow many nm cables but I have not seen them.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Can you lower (or raise) the panel, bring the NM thru the top/bottom, then build a chase around the wiring so that it's still concealed? Why would a gutter underneath be the same problem as you have now? (a pic or two would help)
 

JEI

Member
Location
CA
Can you lower (or raise) the panel, bring the NM thru the top/bottom, then build a chase around the wiring so that it's still concealed? Why would a gutter underneath be the same problem as you have now? (a pic or two would help)

that could work. Just with a 6" gutter it would be clean and I could knock all the holes out befor I mounted. And keep the panel cleaner with out a bunch of holes in it
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you have to drill a bunch of holes thru the back of the panel and thru the siding then you will have a terrible install. IMO, the nipple is a better way to go so as to not destroy the integrity of the siding
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Can you lower (or raise) the panel, bring the NM thru the top/bottom, then build a chase around the wiring so that it's still concealed? Why would a gutter underneath be the same problem as you have now? (a pic or two would help)


If you have a gutter you still need to bring all the cables into it. There is not a good way to do that-- may as well use the panel instead of a gutter.
 