JohnE
Senior Member
- Location
- Milford, MA
Hi Guys,
A buddy of mine has a dilemma. He has wired a pool motor in a one family dwelling by running romex through the unfinished basement and changing over to PVC outdoors to the motor.
This is permitted by 680.21 A(4):
680.21 Motors.
(A) Wiring Methods. The wiring to a pool motor shall comply with (A)(1) unless modified for specific circumstances by (A)(2), (A)(3), (A)(4), or (A)(5).
.....
(4) One-Family Dwellings. In the interior of dwelling units, or in the interior of accessory buildings associated with a dwelling unit, any of the wiring methods recognized in Chapter 3 of this Code that comply with the provisions of this section shall be permitted. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly.
The inspector has failed him citing 680.21(A)1:
680.21 Motors.
(A) Wiring Methods. The wiring to a pool motor shall comply with (A)(1) unless modified for specific circumstances by (A)(2), (A)(3), (A)(4), or (A)(5).
(1) General. The branch circuits for pool-associated motors shall be installed in rigid metal conduit, intermediate metal conduit, rigid polyvinyl chloride conduit, reinforced thermosetting resin conduit, or Type MC cable listed for the location. Other wiring methods and materials shall be permitted in specific locations or applications as covered in this section. Any wiring method employed shall contain an insulated copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG.
Type MC cable listed for the application is permitted as a wiring method for swimming pool motor circuits. This listing requirement ensures that the MC cable is suitable for the environmental and installation conditions typically encountered with swimming pool pump motors. Type MC cables listed for installation in direct sunlight or direct burial are marked to indicate suitability for such applications.
Other than cable assemblies installed on the interior of a one-family dwelling per 680.21(A)(4), wiring methods used for the supply circuit to a swimming pool pump motor must include an insulated, copper equipment grounding conductor not less than 12 AWG.
My friend showed him these sections and tried to explain that 680.21(A)4 allows this install but the inspector told him that (A)1 doesn't allow it....:-?
I guess my reason for posting this is to confirm that I am reading this section properly, and to ask many of you guys respond so that my friend can show him this thread. There are only 2 alternatives: 1. My buddy redoes the install. 2. My buddy takes the inspector to the State Board of Examiners. This seems a little extreme.
I know the inspector and thought about calling him. I'm just not sure how that would go over with him.
Any other thoughts will be appreciated as well.
Thanks,
John
A buddy of mine has a dilemma. He has wired a pool motor in a one family dwelling by running romex through the unfinished basement and changing over to PVC outdoors to the motor.
This is permitted by 680.21 A(4):
680.21 Motors.
(A) Wiring Methods. The wiring to a pool motor shall comply with (A)(1) unless modified for specific circumstances by (A)(2), (A)(3), (A)(4), or (A)(5).
.....
(4) One-Family Dwellings. In the interior of dwelling units, or in the interior of accessory buildings associated with a dwelling unit, any of the wiring methods recognized in Chapter 3 of this Code that comply with the provisions of this section shall be permitted. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly.
The inspector has failed him citing 680.21(A)1:
680.21 Motors.
(A) Wiring Methods. The wiring to a pool motor shall comply with (A)(1) unless modified for specific circumstances by (A)(2), (A)(3), (A)(4), or (A)(5).
(1) General. The branch circuits for pool-associated motors shall be installed in rigid metal conduit, intermediate metal conduit, rigid polyvinyl chloride conduit, reinforced thermosetting resin conduit, or Type MC cable listed for the location. Other wiring methods and materials shall be permitted in specific locations or applications as covered in this section. Any wiring method employed shall contain an insulated copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG.
Type MC cable listed for the application is permitted as a wiring method for swimming pool motor circuits. This listing requirement ensures that the MC cable is suitable for the environmental and installation conditions typically encountered with swimming pool pump motors. Type MC cables listed for installation in direct sunlight or direct burial are marked to indicate suitability for such applications.
Other than cable assemblies installed on the interior of a one-family dwelling per 680.21(A)(4), wiring methods used for the supply circuit to a swimming pool pump motor must include an insulated, copper equipment grounding conductor not less than 12 AWG.
My friend showed him these sections and tried to explain that 680.21(A)4 allows this install but the inspector told him that (A)1 doesn't allow it....:-?
I guess my reason for posting this is to confirm that I am reading this section properly, and to ask many of you guys respond so that my friend can show him this thread. There are only 2 alternatives: 1. My buddy redoes the install. 2. My buddy takes the inspector to the State Board of Examiners. This seems a little extreme.
I know the inspector and thought about calling him. I'm just not sure how that would go over with him.
Any other thoughts will be appreciated as well.
Thanks,
John