Hi all,
I have recently seen an installation of a new mini-split HVAC system where a compressor was installed on a pad outdoors next to the house. Insulated refrigerant pipes and 14-3 NM-B wire run from two locations on the second floor, and one on the third floor. These are covered by vertical metal channels screwed to the siding which run from the origins on the second and third floors to about one foot above ground.
At the bottom of these channels, the insulated pipes and wire run to the compressor unit with no protection from the weather. One of these channels is about 10 feet from the compressor, and the other two are within two feet.
Being clearly unacceptable, the homeowner notified the HVAC installer. The HVAC installer offered to run Seal-tite over the NM-B wiring extending out of the vertical channels to the compressor. Would this be safe and up to code?
I had thought that it wouldn't, based on 334.12(B) and the NM-B within the channels. I think the best solution is to replace these runs of wire with UF-B. Does that make sense?
Thanks!
I have recently seen an installation of a new mini-split HVAC system where a compressor was installed on a pad outdoors next to the house. Insulated refrigerant pipes and 14-3 NM-B wire run from two locations on the second floor, and one on the third floor. These are covered by vertical metal channels screwed to the siding which run from the origins on the second and third floors to about one foot above ground.
At the bottom of these channels, the insulated pipes and wire run to the compressor unit with no protection from the weather. One of these channels is about 10 feet from the compressor, and the other two are within two feet.
Being clearly unacceptable, the homeowner notified the HVAC installer. The HVAC installer offered to run Seal-tite over the NM-B wiring extending out of the vertical channels to the compressor. Would this be safe and up to code?
I had thought that it wouldn't, based on 334.12(B) and the NM-B within the channels. I think the best solution is to replace these runs of wire with UF-B. Does that make sense?
Thanks!