Romex for HVAC
If its NM cable, then 60* ampacity is required regardless if the conductor inside is rated for 90* per 334.80. the 90* rating is only to be used for ampacity adjustments. Lets say you are feeding a 50A rated range receptacle, then you would need to install # 6 instead of # 8. I have this discussion all the time with electricians. Even though # 8 is rated at 50A from the 75* column, It's only rated 40A at 60*.