Is Romex cable (NM) allowed above a suspended ceiling in a commercial building?

cite: code reference please.

When is Romex not allowed in commercial buildings -in general not for a specific city -like Chicago.
 
Re: Romex in Commercial Buildings

Is Romex cable (NM) allowed above a suspended ceiling in a commercial building?
No. 334.12(A)(1)
When is Romex not allowed in commercial buildings
334.10(3). NM can not be used in buildings of Type I or II construction.
 
Re: Romex in Commercial Buildings

Hello-
I didn't know that they took out from the 1999 nec
art:336-5 (a)1--
"In any multifamily dwelling or other structure exceeding three floors and above" In the 2002 it's been taken out. So if I have a 5 floor building I can run nm.
 
Re: Romex in Commercial Buildings

Steve,
So if I have a 5 floor building I can run nm
You can run it as long as the building is not of Type I or II construction. Note: there may be local rules that prohibit the use of NM in this application.
Don
 
Re: Romex in Commercial Buildings

Very doubtful you could build a five story that is not type I or II. I don't have my IBC in front of me, but think you would have to be type III plus one hour walls and a fire sprinklered building. It would probably be cheaper to just go type II and sprinklers.
 