I don't believe I can do this, but I seem to remember discussion about this. I want to feed a shed sub panel from a residence with 8/3 romex or NM in the basement, then strip off the sheathing after it enters the LB and down into the conduit underground 30 feet to the shed new sub panel. Detached structure - will drive a ground rod at shed. Can I use this type of wire in this setting if I strip off the outer sheathing where it is in the conduit? it would make my life much easier but I want to do it right in the end.
 

peter d

Senior Member
Location
New England
You can't do this. You must use conductors rated for wet locations like THWN or UF. The conductors inside of NM cable are not rated or marked for use in wet locations.
 

CopperTone

Senior Member
Location
MetroWest, MA
yea, thats what I though. would be much easier though. I'll just jbox it as it enters the basement and change type of conductors for underground. I can put uf cable in conduit though right? for protection reasons.
 

peter d

Senior Member
Location
New England
stickboy1375 said:
Why anyone would want to struggle pulling a cable through a conduit is beyond me...

I agree, although pulling a 12/2 UF through a 3/4 PVC should be cake, but 3 #12's would be easier.

In the OP's case I would definitely use individual THHN/THWN conductors. :)
 

CopperTone

Senior Member
Location
MetroWest, MA
yes a 4 conductor will be used, 8/3 has 4 conductors. the reason for the conduit is it has to go underneath 2 poured walkways so instead of just sleeves the customer wants continuous conduit. Here is what I'm going to do - whatever conductors are cheaper at the supply house I will use (thwn or uf)
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
CopperTone said:
Here is what I'm going to do - whatever conductors are cheaper at the supply house I will use (thwn or uf)

Don't forget to factor in the extra labor involved for pulling the UF.
 