sfav8r
Senior Member
- Location
- San Francisco Bay Area
I was at a call yesterday, which I must go to again today. I ran across something I've never seen and while I can't think of a code reference off the top of my head, it just looks wrong.
Basically, their is NMC running from branch circuits back to the panel. Where the NMC drops from the floor joists down the wall to the panel, it is covered as it should be.
The service panel is on the exterior. There is an 1-1/4 IMC stub that goes from the back of the panel, through the exterior siding. This is where the NMC enters the panel. The sheathing was stripped off of the NMC at the other end (inside the basement) and enters the panel as seperate wires.
There are proper bushings etc. and I must admit the job looks clean, but I've nver seen NMC that "turns into" individual wires.
Is this OK? If I was doing the original installation, I would put a junction box in the basement, run all the NMC to the junction box, then run THHN from the junction box to the panel. But then again that is a bunch more connections that may not be necessary.
I was there to add several new circuits and if the existing setup is not to code, I want to rectify that before I add new circuits.
Thanks!
Basically, their is NMC running from branch circuits back to the panel. Where the NMC drops from the floor joists down the wall to the panel, it is covered as it should be.
The service panel is on the exterior. There is an 1-1/4 IMC stub that goes from the back of the panel, through the exterior siding. This is where the NMC enters the panel. The sheathing was stripped off of the NMC at the other end (inside the basement) and enters the panel as seperate wires.
There are proper bushings etc. and I must admit the job looks clean, but I've nver seen NMC that "turns into" individual wires.
Is this OK? If I was doing the original installation, I would put a junction box in the basement, run all the NMC to the junction box, then run THHN from the junction box to the panel. But then again that is a bunch more connections that may not be necessary.
I was there to add several new circuits and if the existing setup is not to code, I want to rectify that before I add new circuits.
Thanks!