jmsbrush

Senior Member
Location
Central Florida
My question is can you run romex in PVC conduit if its exposed in outside?
I'm reading article 334.12 A exception: What is type 1 and type 2 construction?
 
In regard to your 1st question, look at 334.12(B)(4) and 300.5(B) and 300.9 ..
The result is no Romex in a conduit in a wet or damp location.
 
Well it's more of which Building Code your under, and how they define it.

Here's a cross link to:

"TYPES OF CONSTRUCTION
Comparisons of Various Classification Sources"

Covering all these listed:
"IBC/IFC: UBC/UFC: NFPA: NFIRS: BOCA: SBC:"

COMMON TERMINOLOGY
 