Romex in EMT

Status
Not open for further replies.

Kimura

Member
Location
Delaware
Was hoping to run 14/2 in 1/2" EMT for a 15' run. See nothing in 358.12 around it. Is it permitted ? Coworker says no, but I can't find anything to state it's NOT allowed.

thank you kindly
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Was hoping to run 14/2 in 1/2" EMT for a 15' run. See nothing in 358.12 around it. Is it permitted ? Coworker says no, but I can't find anything to state it's NOT allowed.

thank you kindly
Indoors it's permitted to run NM cable in EMT. You calculate the fill at 53% using the width of the cable as of it were round.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Indoors it's permitted to run NM cable in EMT. You calculate the fill at 53% using the width of the cable as of it were round.
And for the OP, Southwire shows 14/2 as having a width of 0.368", while Table 4 Chapter 9 shows 1/2" EMT has an ID of 0.622". So the fill ratio for a single 14/2 cable in 1/2" EMT is (368/622)^2 = 35%.

In fact it shows 12/2 as having a width of 0.418", so one 12/2 cable would have a fill ratio of (418/622) = 45%.

Cheers, Wayne
 