IMO, these are just transfer grills. A hole in the wall. Not directly connected to the return air system.
The actual return air duct is somewhere else in the dwelling, which is, most likely, directly connected to the furnace.
I approve this installation.![]()
IMO, these are just transfer grills. A hole in the wall. Not directly connected to the return air system.
The actual return air duct is somewhere else in the dwelling, which is, most likely, directly connected to the furnace.
I approve this installation.![]()
Ron a transfer grill would need a grill on both sides. It is not set up that way at all. Looks like the stud space is the plenum which is connected to duct in the basement or crawl.
I just can't see it as a transfer grill.
I have to believe there is a grill on the bottom of the wall. There is no where else for the air to go. The top plate is not cut out.That's the way I see it too based on the description in the OP. Too bad the photo is cut off on the bottom that might provide some further details.
Some HVAC guys prefer to put return air inlets high on the wall, it is a design issue for them, and makes some sense for cooling purposes - warm air will be drawn from near the ceiling and run through the system to cool it. If you draw return from the floor - you never really exchange any the air near the ceiling without additional circulation methods.I have to believe there is a grill on the bottom of the wall. There is no where else for the air to go. The top plate is not cut out.
BTW, thanks for not beating me up on my post!![]()
Kind of a dumb requirement if you think about it. First no wiring methods are permitted in a plenum unless it supplies something acting upon the environmental air or is specifically permitted otherwise. Putting the cable in FMC doesn't change anything here, especially when one considers typical FMC isn't very isolating air flow wise. Putting in a solid walled tube of some sort to create a "non plenum space" makes more sense.Follow up: I had the rough inspection yesterday, and the inspector said that the vertical runs, as well as those that terminate with a box within the air space, need to be put into a sleeve of flexible metal conduit that goes to an area outside of the cold air space. I forgot to ask.. do I need to place anything onto the FMC in that area, such as a red bushing? I realize, of course, I need a proper flex fitting at the box where it attaches to it.