G GreggSpicer Member Oct 26, 2009 #1 Where in the NEC does it state that Type NM cable sheathing needs to be striped off before feeding it into conduit?
Where in the NEC does it state that Type NM cable sheathing needs to be striped off before feeding it into conduit?
C cpal Senior Member Location MA Oct 26, 2009 #2 What code are you on?? !. It will not say you have to strip the sheathing. in fact the 08 may require you don't, if you are in a basement or crawlspace and install it in a raceway per 334.15(C).
What code are you on?? !. It will not say you have to strip the sheathing. in fact the 08 may require you don't, if you are in a basement or crawlspace and install it in a raceway per 334.15(C).
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Oct 26, 2009 #3 312.5(C) is another area that allows NM in conduit, with a number of restrictions, among them being the sheath must be continuous through the raceway.
312.5(C) is another area that allows NM in conduit, with a number of restrictions, among them being the sheath must be continuous through the raceway.
mcclary's electrical Senior Member Location VA Oct 26, 2009 #4 GreggSpicer said: Where in the NEC does it state that Type NM cable sheathing needs to be striped off before feeding it into conduit? Click to expand... NM with no sheath has no ratings.:roll:
GreggSpicer said: Where in the NEC does it state that Type NM cable sheathing needs to be striped off before feeding it into conduit? Click to expand... NM with no sheath has no ratings.:roll: