What is the largest size romex comes in ? Is there anything over #6
Interestingly enough is that SE cable comes in sizes up to 4/0 copper. One of our supplies is now selling 250MCM aluminum SER. They said that it is good for the 200 amp panels when the se cable is rated 60C and not the total load of the panel. I disagree with them on that. 300 mcm would be needed with a load not greater than 190 amps.
Any reason you cant use 4/0 Al for 200amps??
Was looking at 75 degree column..............
When you all start using the 08 NEC you will see that Se cable is rated at 60C when used as a feeder. Unless it carries the entire load of the dwelling then you cannot use 310.15(B)(6)Any reason you cant use 4/0 Al for 200amps??
Was looking at 75 degree column..............
I am trying to help an AC friend who is in a jam to try and get 15 kw heat to a split system. Its a messed up job on a new house that his company did not install. They ran 10-2 to try run a 7.5 kw air handler. No it did not work but somehow got passed. He will have very little space and in an attic so conduit just not happening. I told him i wasn't sure if or where he could get romex #4
Why would you need #4. #6 would be adequate for 7.5kw. With 125% it calculates to about 40 amps. Then you need to add the blower motor which should not be that much. #6 is good for many 10Kw units.
If there is J, I have alot of rework to do![]()
Dennis, where in the 08 does it specify 60 degree?
334.80 said:The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60?C (140?F) conductor temperature rating
#6 is good for 55 amps. I will suggest it and 10 kw. #2 would be needed if he wants 15kw ,that would be fun to fish into a panel.
Your right and i do recall having running into that a few times#6 does not always work for 10kw. I have seen some 10 kw units that have a mca of 56 amps. Usually a 10kw unit is not really 10 kw. The elements are often 9.6kw or 9.8 but when you add in the blower it can be over 55 amps.