How can I prove to an inspector that Romex staples do not need to be UL listed?
How can I prove to an inspector that Romex staples do not need to be UL listed?
I would say that the staples only needed to be identified which may or may not include a specific listing. We've been using these for a while. They're UL listed and the longer ones are listed for securing two cables at a time.
http://www.brisconelectric.com/catalogPages/3_SScableStaples.pdf
Identified (as applied to equipment). Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Code requirement.
Nonmetallic-sheathed cable shall be secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable at intervals not exceeding 1.4 m (4? ft) and within 300 mm (12 in.) of every cabinet, box, or fitting. Flat cables shall not be stapled on edge.
Hold on! The NEC requires that very few things be "Listed". There are some things that are, such as luminaires (light fixtures). Other things are required to be "identified" such as circuit breaker handle ties. However, EVERYTHING must be APPROVED. The article 100 definition of approved is "acceptable to the authority having jurisdiction" (AHJ). Many AHJ's base their "approval" on the UL or other listing. In this case, the AHJ (assuming the inspector is, in fact the AHJ) has not approved your staples. You must either convince him that they are suitable, or find out who the real AHJ is and have them override the inspector. This is not a function of the NEC, you will need to rely on manufacturer literature, etc to make your case that these staples are suitable, or that no "listed" staples are available.
I had to actually look at your location to see if you were from another country, laws do not work like that here in the United States, before a code can be enforced it must be adopted into law, ...it better be adopted into law or it is not enforceable under the Constitution of The United States, we do not live in a dictatorship country we have laws that all must follow.
My feelings in a nut shell is don't walk on the very Constitution that so many of our fellow Americans have died to protect.
We need to educate ourselves on not only the code we must follow, but the laws that pertain to the enforcement of them, other wise we are at the mercy of what ever we are told to do, and this is not fair to our customers or ourselves when we are forced to add cost un-nessasarlly to a job for something not legally required, just because we are told it is their wish for us to do it that way.
Wayne, 110.2 does not say that, it supports Haskindm's statement. Listing does not guarantee approval. According to 90.7, listing is a convenience to an AHJ to speed approval, it does not legally bind them to approve listed material.
NEMA motors aren't listed for "ordinary locations" although UL has had a standard (UL 1004) for years. Some, but not all, applicable motors are listed for classified locations. Most motors are "recognized components" if they have any label at all and that "label" does not satisfy, the NEC definition of label....We've seen some expansion over time as either manufacturers desired some form of listing solely for marketing advantage (hot tubs), or code changes have made it a requirement (Christy boxes). It's still a fact, though, that some of the highest-quality electrical equipment is not listed by anybody (Baldor motors for one example)...
...... Heck, I'm surprised they don't want listed hangers mounted with listed screws (using a listed driver) to listed studs attached to a listed foundation ..... just where will this silliness end?....