dana1028

Senior Member
Re: Romex

(1999) Section 336-26
"The 90 degree rating shall be permitted to be used for ampacity derating purposes provided the final derated ampacity does not exceed that for a 60 degree rated conductor."
 

charlie

Senior Member
Location
Indianapolis
Re: Romex

334.80 Ampacity. The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60?C (140?F) conductor temperature rating. The 90?C (194?F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60?C (140?F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Romex

You can use the 90 Deg C rating for derating only, but the final ampacity can not exceed the 60 Deg C rating. The conductors are rated at 90 C but jacket is rated at 60 Deg. NEC Section 334.80 lays it out very clearly.
 