I am wondering if there is a temperature limitation to instally nm cable? the temperature outside is 5 degrees. Thanks you
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Some manufactures of PCV type cables and conductors have statements that you are not to install the product if the temperature is less than 14?F.
 

BAHTAH

Senior Member
Location
United States
nm cable outside

nm cable outside

I am wondering if there is a temperature limitation to instally nm cable? the temperature outside is 5 degrees. Thanks you

What type of NM cable? If its NMB "romex" like you use indoors it is not listed to be used outside even if it is in conduit.
 

Mule

Senior Member
Location
Oklahoma
Burr!!! If you have to work in that kind of weather,and your concerned about the wire.... keep your spools in something warm.....blow a heater on it...or if it was me...Id be blowing the heater on "ME" and the heck with the NM
 