Hello There,
I have been drug into a project in which several existing Roof top AC units are going replaced with new slightly smaller units. Not rocket science but I always manage to make things complicated.
For each unit:
* The existing breaker in the panelboard and the wiring from panelboard to roof will re-used.
* A new fused disconnect will be installed on roof.
* New wiring from fused disconnect to new unit.
AC Unit information: 460V, MCA = 22.5A, MROPD = 30A. I do not have any specific motor information. I do not have any LRC information.
- So I need 30A fuses in my disconnect.
- I need #10 conductors from disconnect to new unit.
Where I am getting a little hung up is the hp rating of the disconnect. From what I understand, I need an amp rating of 115% * MCA and a hp rating that is equal to whatever the equivalent horsepower is. Is this correct?
If so, I come up with an equivalent hp of 20 based on MCA of 22.5A. For a Heavy Duty GE Safety switch I would require a 60A rated switch. For 30A fuses, I would need fuse reducers which I try to avoid.
Any feedback appreciated. Thanks.
I have been drug into a project in which several existing Roof top AC units are going replaced with new slightly smaller units. Not rocket science but I always manage to make things complicated.
For each unit:
* The existing breaker in the panelboard and the wiring from panelboard to roof will re-used.
* A new fused disconnect will be installed on roof.
* New wiring from fused disconnect to new unit.
AC Unit information: 460V, MCA = 22.5A, MROPD = 30A. I do not have any specific motor information. I do not have any LRC information.
- So I need 30A fuses in my disconnect.
- I need #10 conductors from disconnect to new unit.
Where I am getting a little hung up is the hp rating of the disconnect. From what I understand, I need an amp rating of 115% * MCA and a hp rating that is equal to whatever the equivalent horsepower is. Is this correct?
If so, I come up with an equivalent hp of 20 based on MCA of 22.5A. For a Heavy Duty GE Safety switch I would require a 60A rated switch. For 30A fuses, I would need fuse reducers which I try to avoid.
Any feedback appreciated. Thanks.