Can be but may not give the desired results. Those systems inherently have some leakage and a 5 ma GFCI is lilely to trip where as a 30ma GFP will not.
 
OK great. I was trying to figure out how to do GFP with AFCI. Now I can just do a dual function breaker. Other than that I could do a GFP breaker with a faceless AFCI device next to the panel.
 
I am somewhat surprised that your cables or the controlling device would be in an AFCI required area. but we don't see many deicing installs in TN.
 
Can be but may not give the desired results. Those systems inherently have some leakage and a 5 ma GFCI is lilely to trip where as a 30ma GFP will not.
I have always wondered about that given the following instruction from Raychem heat trace.
A clean, dry, properly installed circuit should measure thousands of megohms, regardless of the heating cable length or measuring voltage (0–2500 Vdc). The following criteria are provided to assist in determining the acceptability of an installation where optimum conditions may not apply. All insulation resistance values should be greater than 1000 megohms.
With a required start up megger reading of 1000 meg, it should never trip a GFCI.
 
I am somewhat surprised that your cables or the controlling device would be in an AFCI required area. but we don't see many deicing installs in TN.
Massachusetts has amended the 2020 Code to require AFCI on all 15 & 20 amp 120 volt branch circuits supplying outlets or devices in a dwelling. The customer wants a switch device inside the dwelling.
 