Hi,
per my calculation ,
Considering that the total load on the roof mounted panel which is 105A,
using temp. djastm/derating , 142 Deg ., 65% of ampacity of 3/0 cu wire which is 145 amp.
inspector told us to use 150A breaker in the 3ph service to protect that panel through the 3/0 conductors
NOT 200A breaker.
is he right????