Question about derating.
I have 4 units mounted on the roof, and are all rated at 40 amp MAX Fuse size, with a MCA of 32 A.
There is an existing 1-1/4" conduit that I want to use to bring up these circuits, which I can legally fit (12) #6 . When derating #6 THWN wire (12 CCC in a conduit is 50% derating), I Come up with 37.5 amps. Just want to confirm that I am basing this off of of the MCA, and not the max fuse size?
For connecting these equipment, where in the code allows us to use the 75 degree column for connections. or is this a equipment rating?